Hi Group,

Can you folks tell me if, under normal operating circumstances, is intrinsically safe wiring (explosion proof receptacles and light fixtures) required in a welding booth?

We have a tech school near here that has what looks like to me to be explosion proof light fixtures in the booth they use for stick and gas welding, but the receptacles are the standard 15 amp residential type.

Any opinions / help you can offer will be greatly appreciated!!!
 
Last edited:

muskiedog

Senior Member
Location
Minnesota
There may be a dust concern See the osha web under general requirements

There may be a dust concern See the osha web under general requirements

Welding, Cutting, and Brazing
? Standard Number: 1910.252
? Title: General requirements.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Loss Control Consultant said:
Hi Group,
Can you folks tell me if, under normal operating circumstances, Intrinsically Safe Wiring (explosion proof receptacles and light fixtures) are required in a welding booth?
There is no such thing as an intrinsically safe light fixture or receptacle.
I see no reason for welding booth to require explosion proof wiring methods. Are you sure the fixture is not just a vapor proof for protection of the lamp?
 
don_resqcapt19 said:
There is no such thing as an intrinsically safe light fixture or receptacle.
I see no reason for welding booth to require explosion proof wiring methods. Are you sure the fixture is not just a vapor proof for protection of the lamp?


Thanks for the guidance. You're right. I'm not sure the existing light fixtures are explosion proof. This demonstrates my lack of knowledge. I am probably not even using the term "intrinsically safe " correctly.
 

cschmid

Senior Member
Loss Control Consultant said:
Thanks for the guidance. You're right. I'm not sure the existing light fixtures are explosion proof. This demonstrates my lack of knowledge. I am probably not even using the term "intrinsically safe " correctly.

intrinsically safe is an installation that ensures that the electrical installation and equipement involved in the installation are so designed that it can not produce a spark in the exsplosive enviroment it is installed in..I hope I have described that correctly..
 