Hi all,
I am installing an AC disconnect for an inverter output to comply with the NEC 690.14. The inverter's maximum AC output is 36.2 A. Can I just to a 40A disconnect (https://www.bentek.com/wp-content/uploads/ds/991-004409-000-B_Bentek-Disc-AC-DS.pdf) or should I do the 1.25 derate (36.2 x 1.25 =45.25 A) and use a 50A disconnect?
Is there an NEC code that explains if the 1.25 derate is required.
Thanks!
I am installing an AC disconnect for an inverter output to comply with the NEC 690.14. The inverter's maximum AC output is 36.2 A. Can I just to a 40A disconnect (https://www.bentek.com/wp-content/uploads/ds/991-004409-000-B_Bentek-Disc-AC-DS.pdf) or should I do the 1.25 derate (36.2 x 1.25 =45.25 A) and use a 50A disconnect?