Shaneyj
- Katy, Texas
- Project Engineer
Hello All.
A scenario came up at work today and my EE could not give me a concrete answer. After an attempt at research, neither could google.
I'm installing an inverter on a unit for a customer. This is a refurb, and the customer is upgrading from a 1500W to a 5000W inverter.
The existing wiring is 4awg supplied by (4) 12VDC batteries wired in parallel.
The inverter specs call out either parallel 1/0 or single 4/0 to supply the inverter.
I wanted to figure DC current for my own education and curiosity, but after some inquiry to my EE and google, I found conflicting information.
Several online ac to dc current calculators seemed to be using the simple 1:1 inverse relationship of V to I found in transformer calcs.** using this the 5kW @ (120VAC)= 41A. 12VDC primary to 120VAC secondary is a 1:10 ratio, so the DC current would calculate to be 10*41A= 410A DC.
I did find more than one source that quoted dc current to be 63% of ac current, but this seems to be going the wrong direction.
I hope this is not too disjointed... On to my questions.
I have been unsuccessful in tracking down a formula to calculate the DC current with respect to the current of the AC load. Does one exist where I can plug in my variables, (i. e., source voltage, load voltage, etc.) to determine whatever unknown exists?
Also, are there literature that specifies the differing ampacity ratings of conductors when dealing with DC as opposed to AC?
Thanks in advance to all who weigh in.
P. S. I've been reading this forum for over a year and this is my first post... It has added to my education. Thanks to all who support it.