Who out there has been requested to install backup power transfer switches in residences with the customer desiring to use an inverter generator?
The attraction is quieter generator and better fuel economy.
There are a couple of technical issues on inverter generators. Honda, Yamaha, and Robin inverter generators do not have a groundable common on their A.C. output. This is because of the H-bridge Pulse Width Modulator that produces the 60 Hz output. Second issue is they are only 120 vac output.
I see two possible solutions, both require an isolation transformer to allow common-ground connection at breaker box.
First is 120 v to 240/120 v isolation transformer to provide L1,L2 sides for auxilary breaker box.
Second is 120 v to 120 v isolation transformer having transfer switch that connects L1,L2 sides of auxilary breaker box together when on backup generator. This would have to be restricted to no 240v service breaker ports in auxilary box but can still maintain L1-L2 load balancing when on mains. Not sure what code says about this approach.
The attraction is quieter generator and better fuel economy.
There are a couple of technical issues on inverter generators. Honda, Yamaha, and Robin inverter generators do not have a groundable common on their A.C. output. This is because of the H-bridge Pulse Width Modulator that produces the 60 Hz output. Second issue is they are only 120 vac output.
I see two possible solutions, both require an isolation transformer to allow common-ground connection at breaker box.
First is 120 v to 240/120 v isolation transformer to provide L1,L2 sides for auxilary breaker box.
Second is 120 v to 120 v isolation transformer having transfer switch that connects L1,L2 sides of auxilary breaker box together when on backup generator. This would have to be restricted to no 240v service breaker ports in auxilary box but can still maintain L1-L2 load balancing when on mains. Not sure what code says about this approach.