If I have a 110 V 5000 Watt Inverter with 10000 Watt surge, My question is, At 12 V input, how many DC amps would be required to maintain that 110 AC 5000 Watt Inverter output assuming it were constant at 5000 Watts?
I am trying to calculate and choose the proper batteries and amps for this purpose and do not know how to calculate it. I will be using Trojan 6 volt or maybe 12 volt deep cycle batteries.
Thanks
Daniel
I would ball park it around 460 amps.
5000 watts / 12 VDC = 416 amps, if you are lucky maybe 90% efficient.
416/.9= 462 amps.
Of course I am just a hack, one of the engineers may prove me wrong. :)
Thanks, I took a stab at 90% based on my experience with PV inverters but I think there could be a large range depending on how much the OP spent for the inverter.
You can approximate inverters like transformers. With a 1:10 voltage ratio, you'd have a 10:1 current ratio.
For each amp at 120v, figure 10 amps at 12v.
I would have guessed the efficiency of the inverter being lower though.
Actually, many are higher, especially near full load.