Shockedby277v Senior Member Location Michigan Apr 26, 2023 #1 Can power from an inverter be mixed with utility power for lighting in the same raceway? Can power from a generator (life safety) and utility also be mixed in the same raceway for lighting?
Can power from an inverter be mixed with utility power for lighting in the same raceway? Can power from a generator (life safety) and utility also be mixed in the same raceway for lighting?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Apr 26, 2023 #2 No conductors covered by Article 700 can be in the same raceway as conductors of other systems.