Inverter Running at 66% or Transformer

Status
Not open for further replies.
The general rule of thumb is that there is little penalty for bucking and a more significant penalty for boosting..... and a 240Vac system needs ±340Vdc. Just ballpark figures but it gives an idea.


So here in the northeast where it's cold, some quick and dirty calcs show it's actually tough to keep array voltage above the peak voltage for a 240v system with 600 volt strings.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
So here in the northeast where it's cold, some quick and dirty calcs show it's actually tough to keep array voltage above the peak voltage for a 240v system with 600 volt strings.
Funny, I always thought that the string voltages (both VOC and VMP) rise as temperature decreases. That is why you need to know the minimum operating temperature (usually just after dawn on a clear winter night) and the temperature coefficient of voltage with temperature to make sure that the maximum input voltage of the inverter is not exceeded.
Or do you mean that by keeping the winter voltage safe you are perhaps reducing the summer noon voltage below the minimum operating voltage?
 
Funny, I always thought that the string voltages (both VOC and VMP) rise as temperature decreases. That is why you need to know the minimum operating temperature (usually just after dawn on a clear winter night) and the temperature coefficient of voltage with temperature to make sure that the maximum input voltage of the inverter is not exceeded.
Or do you mean that by keeping the winter voltage safe you are perhaps reducing the summer noon voltage below the minimum operating voltage?


Yeah the latter. Figuring around -25 F for a low and hot summer day in the sun around 130 results in a very wide voltage range.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
Yeah the latter. Figuring around -25 F for a low and hot summer day in the sun around 130 results in a very wide voltage range.

That's why the first generation SMA transformerless inverters were such a pain here in Texas. Usually there was only one string length that would work, and even then if the grid were to glitch in the middle of the day the PV system would not restart until the next morning.
 