I'm swapping out 4 2800 pv power with 4 sunny boy 3.0-us inverters, existing inverters did not utilize a neutral , my new inverters manual says I don't need a neatral if my grid is 208 delta connection I'm not to good with transformers. I know I don't have a high leg. I believe we have a 208 wye. What is 208 delta connection thank you
A 208 delta connection means that you wire your circuits across adjacent phases, instead of from phase to neutral.
The first inverter connects on a 2-pole breaker to A & B.
The second inverter connects on a 2-pole breaker to B & C.
The third inverter connects on a 2-pole breaker to C & A.
To calculate the combined current of many inverters wired in such a manner, add up all connected to AB, then BC, then CA.
Ia = sqrt(Iab^2 + Ica^2 + Iab*Ica) + Ian
Ib = sqrt(Iab^2 + Ibc^2 + Iab*Ibc) + Ibn
Ic = sqrt(Ibc^2 + Ica^2 + Ibc*Ica) + Icn
Iab = current on circuits connected between phases A & B
Ian = current on circuits connected between phase A & the neutral
Size all aggregate equipment for the maximum of the above.