PV systems are designed that way intentionally. Conductors and OCPD are sized so that conductors cannot be damaged and OCPD cannot be tripped by the maximum inverter output current.Can the inverter even source enough fault current for this to be an issue? As I recall, they typically cannot source enough current to operate the output side OCDP in the instantaneous trip range.
The 4000A breaker will need to have ERMS to be compliant, irrelevant on being fed from an inverter.I'm not an engineer, so I can't answer that question. 240.87 calls for it, and there doesn't seem to be an exception. It's the first time I've seen an inverter with a 4000 amp breaker. First time I've seen an inverter this large.
It seems to me that this would be covered by (B)(5)How do inverters comply with 240.87 arc-reduction? Is it built into the inverter? Do AHJs require this? There doesn't seem to be an exception for PV. 2020NEC
This poses the "look inside the box" question. Can an AHJ look inside a piece of UL Listed equipment and point to something and say, this does not comply with the NEC? The answer is no, see NEC 90.7. The CB inside a UL Listed inverter is assumed to comply with the NEC when the inverter is installed in accordance with the manufacturer's installation instructions.How do inverters comply with 240.87 arc-reduction? Is it built into the inverter? Do AHJs require this? There doesn't seem to be an exception for PV. 2020NEC
Wow, great point. But is UL listing assumed to meet current NEC code? I would think the UL test is just to make sure the equipment does what it says, in this case safely inverting the voltage. Do they also look for code requirements like arc-energy reduction? Or does the NEC just not apply?This poses the "look inside the box" question. Can an AHJ look inside a piece of UL Listed equipment and point to something and say, this does not comply with the NEC? The answer is no, see NEC 90.7. The CB inside a UL Listed inverter is assumed to comply with the NEC when the inverter is installed in accordance with the manufacturer's installation instructions.
Generally they are separate spheres and the NEC does not apply. Which I think can be said in this case. But there is also some harmonization of UL standards and the NEC and ways they look to each other. I would be somewhat surprised if there wasn't already something in UL standards about arc-energy reduction. That seems like a 'standardsy' thing that's making it's way into the NEC and not vice versa. But I could be wrong.Wow, great point. But is UL listing assumed to meet current NEC code? I would think the UL test is just to make sure the equipment does what it says, in this case safely inverting the voltage. Do they also look for code requirements like arc-energy reduction? Or does the NEC just not apply?
This....or say that 240.87 doesn't apply as the OCDs are part of UL approved equipment (90.7)?
No, the code is pretty clear. See first sentence of second paragraph of 90.7.Seems like the Code needs some clarification on this.
The inverter manufacturer doesn't know if you will use one of the alternate compliance methods for 240.87, so if they don't install arc flash reduction maintenance switch in the 4000A CB, that doesn't relieve the designer / installer to still comply with 240.87So the bottom line is how to make sure the installation complies with 240.87? Require info that the UL listing confirms compliance, or say that 240.87 doesn't apply as the OCDs are part of UL approved equipment (90.7)? Seems like the Code needs some clarification on this.
This is incorrect. The designer does not have to evaluate what is in the UL Listed box for NEC compliance. That is made very clear in 90.7 and applying 240.87 would require evaluating the internal OCPD. When a UL Listed device requires extra outside equipment to be installed it will state so in the installation documentation. For instance, the installation documentation for inverters that can be interconnected to ungrounded utility sources will often have as an additional requirement the installation of an external ground fault detection device since the inverter usually does not have one included.The inverter manufacturer doesn't know if you will use one of the alternate compliance methods for 240.87, so if they don't install arc flash reduction maintenance switch in the 4000A CB, that doesn't relieve the designer / installer to still comply with 240.87