Carultch
- Massachusetts
The example is carport canopy columns, used as support structures for inverters. Elevated out of reach of the general public, site personnel would need a ladder to service each inverter.
It is my understanding that for an inverter in such a location needs "comprehensive disconnects" within sight and readily accessible relative to the location of the inverter. So you are up on the ladder, you should be able to reach both AC and DC disconnects without a tool, and without getting off the ladder. Am I understanding this correctly?
The question is, can this disconnect be behind a latched opaque enclosure lid? Provided that the cover is permanently labeled to mark that it is a disconnect. Not a screw cover, but a quick-release latch.
The string inverters I'm specifying only have DC disconnects without a DC combiner, and would thus need an external DC combiner and AC disconnect in addition. I'd like to build a custom enclosure with the combiner fuses and busbars, as well as a DIN-rail mounted AC breaker, to satisfy both requirements in one enclosure. And not have to insert a disconnect through the lid.