The covers that qualify have been around a long time, code finally changed to allow them without a bonding jumper more recently.Oh yeah those raised cover w the dimples came in about maybe 5/6 years ago and there's a new rule for them! Thanks guys
I'll doublecheck with my inspector
Thx!
In belief, man can do anything
Correct, always needed to make sure the box was bonded first then you may or may not need jumpers to devices, covers, etc. depending on other rules and conditions.People get this confused about jumpers, both with the raised covers with the flat spots for mounting and any other metal box. It is/was thought that you brought the EGC to the device (recep or switch) and then jumper to the box if needed. That is wrong, you have to land the EGC in the box then either it needs a jumper to the device or not depending on the circumstances.
Simply put, EGC to the box then if jumper is needed it goes to device, not the other way around.