Hello,
My apologies for bit lengthy b7t wanted everyone to have an idea of what I came across.
I recently upgraded a residential overhead service from 100 to 200 amp with a subpanel.
Poco renergized system. Like a Newby I didn't confirm voltages at that time. Turned on main breaker and sub panel breaker. Lights worked, receps, oven, etc.
Left jobsite. Customer called said kitchen breaker kept tripping. Checked VAC at single pole breaker on phase B to find 243 v to neutral.
Checked main breaker and have phase A to neutral 120, phase B 243 to N.
Phase to phase reads 122. Poco just dropped service at mast, not at transformer.
Has anyone else ever experienced such a thing?