Are you referring to 250.32? What part of that section would allow this?Feeder to a seprate building, disconnect on exterior of building with 4/0 ser feeding a main lug panel. Wanting to utilize the 2/0 equipment ground as the g.e.c as this seems to be allowed by the exception (2017 nec).
Only have the 2020 at my desk, but we are on the 2017. 250.121 exceptionAre you referring to 250.32? What part of that section would allow this?
I have thought about those, but i am not sure they are listed for groundingH tap connectors are more commonly used in utilities but may work on your application. The specific one I referenced here isn’t UL listed but is CSA listed. You may look at what Burndy or others have.
I'm confused here.Feeder to a seprate building, disconnect on exterior of building with 4/0 ser feeding a mainlug panel. Wanting to utilize the 2/0 equipment ground as the g.e.c as this seems to be allowed by the exception (2017 nec). Need to continue on from the panel location to the water service entrance, was looking for a crimp connection to go from 2/0 to #4 solid bare
H taps have separate grooves for each conductor and accept copper or aluminum conductors, but they likely not listed for what OP wants to do.You can't just crimp copper to aluminium can you?