electricalist
Senior Member
- Location
- dallas tx
When and where are they required?
Sent from my iPhone using Tapatalk
Sent from my iPhone using Tapatalk
250.64(C) Continuous. Except as provided in 250.30(A)(5) and
(A)(6), 250.30(B)(1), and 250.68(C), grounding electrode
conductor(s) shall be installed in one continuous length
without a splice or joint. If necessary, splices or connec-
tions shall be made as permitted in (1) through (4):
(1) Splicing of the wire-type grounding electrode conduc-
tor shall be permitted only by irreversible compression-
type connectors listed as grounding and bonding equip-
ment or by the exothermic welding process.
(2) Sections of busbars shall be permitted to be connected
together to form a grounding electrode conductor.
(3) Bolted, riveted, or welded connections of structural
metal frames of buildings or structures.
(4) Threaded, welded, brazed, soldered or bolted-flange
connections of metal water piping.
In my other thread the AHJ didn't care about any GES for PV. This one wants it followed to the letter including. Brown and yellow wire for the D.C. side.