I am installing a 45KW single phase generator, and connecting it to a 400a single phase residential service. The existing service has 2 200A main panels, connected to 1 400a meter with no disconnects. I installed 2 200A service rated ATS's between the meter and main panels.
Was not thinking ahead, the single grounding conductor from the generator needs to be a irrevsible splice.
I need to find a method to splice 3 aluminum conductors in a trough before going into the ATS's. Local inspector has no input, and does not have any recommendations. Local supply house doesn't have any ideas either??
Any ideas or recommendations would be a huge help.
Thanks