rt66electric
Senior Member
- Location
- Oklahoma
Newly installed propane pump/motor
explosion proof motor
operation temp at center of motor mass running at 145 deg F(FLIR camera)
ambiant temp 95 deg F
temp at bearings approx 100 deg F
pump running cool
line running amps .. 8 amps 2hp motor.
is this too high??
what is max temp before internal overtemp kicks in???
other notes
distance from 15 amp shunt trip breaker is approx 300ft using #8 wire with no splices from breaker to on/off switch, then 20 ft to motor.
another concern is 230volt motor on a 208 circuit.
another concern, a quick turn on/turn off will trip the breaker.
I have rewired entire branch circuit. Previous electrician ran #12 THHN , the old pump lasted approx 1 Year
Any thoughts or suggestion???
Thank You
Dennis
explosion proof motor
operation temp at center of motor mass running at 145 deg F(FLIR camera)
ambiant temp 95 deg F
temp at bearings approx 100 deg F
pump running cool
line running amps .. 8 amps 2hp motor.
is this too high??
what is max temp before internal overtemp kicks in???
other notes
distance from 15 amp shunt trip breaker is approx 300ft using #8 wire with no splices from breaker to on/off switch, then 20 ft to motor.
another concern is 230volt motor on a 208 circuit.
another concern, a quick turn on/turn off will trip the breaker.
I have rewired entire branch circuit. Previous electrician ran #12 THHN , the old pump lasted approx 1 Year
Any thoughts or suggestion???
Thank You
Dennis