R Ray G. Member Location Aspen CO. USA Dec 11, 2017 #1 Is 4/0 thhn/thwn alu. with 75 degree lugs permitted for a 200 amp commercial service
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Dec 11, 2017 #2 Is the calculated load 180A or less per 230.42? If so, then yes.
electrofelon Senior Member Location Cherry Valley NY, Seattle, WA Occupation Electrician Dec 11, 2017 #3 I concur with Derek. The key is you get to use the next size up rule 240.4 B