mike33:
What is the real question here?
We will assume a high input impedance DVM, like a Fluke 27 or 87, and a typical residential environment.
Try these experiments:
1. Select the normal AC voltage range. Plug in the two test leads. Hold them up in the air with your arms spread apart, and without touching the probe tips. What voltage do you read?
2. Put one lead in the neutral of an outlet, and hold the other probe in the air. What do you read?
3. Same as 2 but put the one lead in the hot side of the outlet. What do you read?
4. Roll out a 50 ft or so extension cord on the floor. Connect the extension cord to nothing, except one wire to the meter. Connect the other meter lead to neutral or ground. What do you read?
All of these voltages read are a result of capacitive coupling.
If you put a moderately low resistance, like a 25 W incandescent bulb, across the meter input, then the voltage will drop to a low level.
.