By single main I am referring to how the internal bypass (static switch) is connected via internal bus links to the main input, and the overall UPS system is fed from a single 3-ph 3-wire 480 V AC source.
According to IEEE 3003.1-2019 9.5, the answer is simply no, because "Transformerless UPS units do not provide electrical (galvanic) isolation between the UPS ac output and its ac input. As such, transformerless UPS units should not be treated as a separately derived system. Any ground-fault current on the output of the transformerless UPS returns to the source of the ac input and not the UPS inverter output." There is similar language in 9.2.
It appears this covers only normal operation. Consider either the upstream UPS input circuit breaker being opened unexpectedly, or if the UPS is applied in conjunction with a standby diesel generator, then during the brief period of time during the break-before-make transition between sources: the UPS is still providing power downstream via battery/inverter, but is presumably operating ungrounded (no neutral being brought to the UPS since it is a 3-wire system)? You can find some information online saying that due to the duration of exposure this is a non-issue, which seems reasonable, but it seems to be something worth considering. It also looks like some UPS manufacturers provide the required ground detection circuity per 250.67.
It's a bit funny to install a UPS to provide backup power in such scenarios, but then for it's classification as a separately derived source to change resultingly.
Posting to encourage some discussion, maybe I am interpreting things wrong.
According to IEEE 3003.1-2019 9.5, the answer is simply no, because "Transformerless UPS units do not provide electrical (galvanic) isolation between the UPS ac output and its ac input. As such, transformerless UPS units should not be treated as a separately derived system. Any ground-fault current on the output of the transformerless UPS returns to the source of the ac input and not the UPS inverter output." There is similar language in 9.2.
It appears this covers only normal operation. Consider either the upstream UPS input circuit breaker being opened unexpectedly, or if the UPS is applied in conjunction with a standby diesel generator, then during the brief period of time during the break-before-make transition between sources: the UPS is still providing power downstream via battery/inverter, but is presumably operating ungrounded (no neutral being brought to the UPS since it is a 3-wire system)? You can find some information online saying that due to the duration of exposure this is a non-issue, which seems reasonable, but it seems to be something worth considering. It also looks like some UPS manufacturers provide the required ground detection circuity per 250.67.
It's a bit funny to install a UPS to provide backup power in such scenarios, but then for it's classification as a separately derived source to change resultingly.
Posting to encourage some discussion, maybe I am interpreting things wrong.