jeremysterling
- Austin, TX
I installed a breaker enclosure in an equipment room. It has one 200A 3 pole shunt trip bkr with NO/NC aux contacts. Would this enclosure fall under 110.26(e)? Is it considered a switchboard?
IMO no.....jeremysterling said:Is it considered a switchboard?
Switchboard. A large single panel, frame, or assembly of panels on which are mounted on the face, back, or both, switches, overcurrent and other protective devices, buses, and usually instruments. Switchboards are generally accessible from the rear as well as from the front and are not intended to be installed in cabinets.
jeremysterling said:not intended to be installed in cabinets.
Cabinet. An enclosure that is designed for either surface mounting or flush mounting and is provided with a frame, mat, or trim in which a swinging door or doors are or can be hung.
See 110.26(A)(3)What I really need to know is if the 4 square boxes for lighting that I mounted on the wall above the bkr enclosure need to be moved up to 6'6" above the enclosure per 110.26(e)?
jeremysterling said:What I really need to know is if the 4 square boxes for lighting that I mounted on the wall above the bkr enclosure need to be moved up to 6'6" above the enclosure per 110.26(e)?
I'll stick with my thread response, no I didn't read the article stated.jeremysterling said:cadpoint,
the 4 sq boxes are junction boxes for lighting going to a lighting contactor. the lighting contactor is about 110' away...
the bkr enclosure is for elevator equipment.
110.26(A)(3) is about not allowing anything, electrical or otherwise, protruding into the space dedicated to personnel for working space, which could make servicing or repair difficult or hazardous.jeremysterling said:My install is legal, but what if I had mounted an 12X12X12 screw cover box on thick strut above the 6" deep bkr enclosure and exceeded the 6 inches from 110.26(a)(3)? Could I argue that 110.26(e) does not apply?