Looking at the sizing of a Busway Riser in a high rise as part of a peer review and whether or not it was sized correctly. Have looked at Article 220 and Article 215 assuming that it would be considered a feeder. I think that's the case BUT wanted to make sure it didn't fall into some other category and was perhaps NOT subject to Article 215? What do you think?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Looking at the sizing of a Busway Riser in a high rise as part of a peer review and whether or not it was sized correctly. Have looked at Article 220 and Article 215 assuming that it would be considered a feeder. I think that's the case BUT wanted to make sure it didn't fall into some other category and was perhaps NOT subject to Article 215? What do you think?
See Article 368 as well
 