I have 200 A main service panel and want to add a subpanel at an opposite corner of the house. The original owner had a length of 8/3 cable installed in the service panel in anticipation of installing a hot tub. The original owner didn't install the hot tub and the cable is lying dormant midway in the crawl space and the service panel end is not yet connected to any OCPD.
What I would like to do, to save tearing up walls to install a new cable, is to wire the existing 8/3 to a 50 amp, 2 pole breaker at the service panel, install a 60 amp disconnect in the crawlspace to connect the other end of the existing cable and extend from this disconnect to the subpanel, which is another 20 feet away. The disconnect will maintain connected but separate neutral and ground and essentially serves as a high current J box. The subpanel will also have separate Ground and Neutral as per code. The subpanel is locate in the same building so a main lug panel will be used.
I haven't found anything in the code that addresses this. Does anyone have any pointers???
Thanks in advance,
Tom
What I would like to do, to save tearing up walls to install a new cable, is to wire the existing 8/3 to a 50 amp, 2 pole breaker at the service panel, install a 60 amp disconnect in the crawlspace to connect the other end of the existing cable and extend from this disconnect to the subpanel, which is another 20 feet away. The disconnect will maintain connected but separate neutral and ground and essentially serves as a high current J box. The subpanel will also have separate Ground and Neutral as per code. The subpanel is locate in the same building so a main lug panel will be used.
I haven't found anything in the code that addresses this. Does anyone have any pointers???
Thanks in advance,
Tom