I was helping an electrician buddy wire his house. His meter can is by the transformer at the end of his driveway and his service disconnect is on the house. The meter and service disconnect are about 200 ft away from eachother, connected with PVC conduit. The question is, do you need an EGC pulled between the meter and disconnect? I say no because there's no overcurrent device protecting this section of wire, so a EGC does no good. He says yes because he thinks the main breaker will trip from a fault on either the line side or load side of main breaker. I don't think the main breaker will trip from a line side fault. 2 different inspectors looked at it. One said we needed the EGC, the other said we didn't.
Your thoughts?