SysEngAce
Member
- Location
- Knoxville, TN, USA
We have equipment that can be supplied with a range of 3 phase voltages from 380-480 VAC. There is a power distribution cabinet which has a 12 kVA delta to eye isolation transformer with a multi-tap primary where we connect incoming power. The transformer primary does not require the neutral but we have a neutral available. The secondary supplies 3 phase 230 VAC (line to line voltage) and uses the center of the WYE to create a line to neutral voltage.
My question is can I connect the secondary WYE center to the incoming power feed neutral or if it has to be connected to a grounding electrode as a seperately derived system?
Also, if it is ok to connect it to the incoming power neutral does it make the isolation less effective?
My question is can I connect the secondary WYE center to the incoming power feed neutral or if it has to be connected to a grounding electrode as a seperately derived system?
Also, if it is ok to connect it to the incoming power neutral does it make the isolation less effective?