Outlet. A point on the wiring system at which current is taken
to supply utilization equipment.
That would be a great Code proposal !In my opinion, the outlet for all hard wired utilization equipment is the point where the branch circuit conductors connect to the equipment conductors.
So the connected equipment that does not function is not connected to an outlet?
The current definition basically implies that already, in that the branch circuit conductors are part of the (premises) wiring system, and the equipment conductors are part of the utilization equipment, so the connection between the two is the point at which current is taken from one to the other.That would be a great Code proposal !
So I think your proposal reflects a slight change from the status quo as far as outlet location.Public Input No. 174-NFPA 70-2023 [ Definition: Outlet. ]
Outlet.
The point where the branch circuit conductors connect to, or will be connected to, a receptacle, lampholder terminals or conductors, luminaire terminals or conductors, or utilization equipment terminals or conductors. (CMP-1)
I don't think so. Both receptacle outlets and lighting outlets have there own definition saying that they are installed at "generic" outlets.So I think your proposal reflects a slight change from the status quo as far as outlet location.
I would say that current is either in the premises wiring or in the utilization equipment, and it just transitions once, at the outlet. In which case is the receptacle/keyless itself part of the premises wiring or part of the utilization equipment? I would say part of the premises wiring.
Thus at present the outlet is the point of contact between the wipers of a receptacle and the pins of a plug, or between the Edison socket and the bulb. Your PI moves the outlet to be the wiring terminals of the receptacle or the keyless.
Cheers, Wayne
Receptacle Outlet.
An outlet where one or more receptacles are installed. (CMP-18)
Lighting Outlet.
An outlet intended for the direct connection of a lampholder or luminaire. (CMP-18)
I don't find the definitions you quoted to be in contradiction with what I've stated, I'm not sure what you are seeing in them.I don't think so. Both receptacle outlets and lighting outlets have there own definition saying that they are installed at "generic" outlets.
I agree. The NEC does not require a fixture (in most cases) just a lighting outlet.In my inspection reports, when a contractor fails to follow the plans, showing a symbol for an electrical ceiling lighting outlet. I would say:
"The contractor failed to install a ceiling lighting outlet". No fixture, just an outlet.
Is this the correct contexts ?
I am simply saying those items are installed at outlets.I don't find the definitions you quoted to be in contradiction with what I've stated, I'm not sure what you are seeing in them.
Let's make it simple: is a receptacle part of the premises wiring system?
If so, I say that the current definitions pinpoints the outlet to a particular connection, in this case the connection of the attachment plug (part of the utilization equipment) to the receptacle (part of the premises wiring system).
If not, then how do you categorize the receptacle? Neither premises wiring nor utilization equipment? That's certainly consistent with all the definitions quoted so far in this thread, but breaks the nice dichotomy that all of the circuit is one or the other.
Cheers, Wayne
Based on that definition, a receptacle is not really an outlet....just installed at one, so yes a receptacle is neither premises wiring nor utilization equipment.Receptacle.
A contact device installed at the outlet for the connection of an attachment plug, or for the direct connection of electrical utilization equipment designed to mate with the corresponding contact device. A single receptacle is a single contact device with no other contact device on the same yoke or strap. A multiple receptacle is two or more contact devices on the same yoke or strap. (CMP-18)
OK, to me, the definition says an outlet is a point (more properly a surface, a particular connection between two conductors), implicityly with multiplicity (since you need multiple conductors to form a surface). And so "at" a point just means touching that point.I am simply saying those items are installed at outlets.
once again we reach an impasseOK, to me, the definition says an outlet is a point (more properly a surface, a particular connection between two conductors), implicityly with multiplicity (since you need multiple conductors to form a surface). And so "at" a point just means touching that point.
So those definitions saying "at" an outlet are consistent with a receptacle or keyless lamp holder being part of the premises wiring system. I.e. I put the outlet at the utilization equipment side boundary of the receptacle or keyless lamp holder, not at the supply-side boundary of the device.
This interpretation is informed by the definition of Premises Wiring System, which includes wiring devices, which includes receptacles. So the receptacle itself has to be part of the Premises Wiring System.
Cheers, Wayne
once again we reach an impasse![]()