Is a light switch "Equipment foreign to the electrical installation" near a panel?
I'm looking at:
https://www.mikeholt.com/instructor2/img/product/pdf/11NEC101-1076-sample.pdf (which is awesome, BTW).
Figure 110-34 says "raceways and cables" can be located in the dedicated electrical space for a subpanel. But other "equipment foreign to the electrical installation" is known to be prohibited, at least within the dedicated electrical space. Yet Figure 110-32, just above the first figure, suggests a switch is a violation of the NEC because it's a motion sensor, not because it's apparently about 11" from the panel shown. In the case of 110-32, the illustration shows a panel that's wide enough (30") to create its own dedicated working space. Many (probably most) sub-panels are not that wide.
Note the difference, please, between dedicated electrical space and dedicated working space. The former is inside the wall; the latter is for a human standing at the electrical equipment, to service or inspect it.
So is a light switch allowed within the dedicated working space? It hinges on the word "the," really. A light switch would be "equipment foreign to the electrical installation" (i.e., a switch unrelated to the sub-panel, but grounded) as opposed to "equipment foreign to electrical installation" (no "the" here - meaning, typically, a sanitary drain pipe above it).
Switch is okay, or switch is not okay?
Thanks!
I'm looking at:
https://www.mikeholt.com/instructor2/img/product/pdf/11NEC101-1076-sample.pdf (which is awesome, BTW).
Figure 110-34 says "raceways and cables" can be located in the dedicated electrical space for a subpanel. But other "equipment foreign to the electrical installation" is known to be prohibited, at least within the dedicated electrical space. Yet Figure 110-32, just above the first figure, suggests a switch is a violation of the NEC because it's a motion sensor, not because it's apparently about 11" from the panel shown. In the case of 110-32, the illustration shows a panel that's wide enough (30") to create its own dedicated working space. Many (probably most) sub-panels are not that wide.
Note the difference, please, between dedicated electrical space and dedicated working space. The former is inside the wall; the latter is for a human standing at the electrical equipment, to service or inspect it.
So is a light switch allowed within the dedicated working space? It hinges on the word "the," really. A light switch would be "equipment foreign to the electrical installation" (i.e., a switch unrelated to the sub-panel, but grounded) as opposed to "equipment foreign to electrical installation" (no "the" here - meaning, typically, a sanitary drain pipe above it).
Switch is okay, or switch is not okay?
Thanks!