Is a MCB required in this situation?
7kiarider
virgina
Electrical Designer
I am working on a set of apartment buildings and I am torn between needing a MCB in my meter stack or not. Each building will have 24 apartments 12 apartments will be feed from 1200A 13 meter, meter stack from the north side and one from the south side of each building. Each meter stack will be feed from a service transformer. Does NEC 230.71 apply here?
So without a main each side of the building would end up with 13 service disconnects?
Correct, each meter would have their own breaker i am inclined to think we need a main service disconnect ahead of all the meter stacks. Or is each meter considered their own service?
No a meter does split service conductors into multiple services. You are allowed a max of 6 service disconnects, and keep in mind the recent code change that will require them to be in different compartments or enclosures (depending on the type of equipment).