Is a UFER or CEE required to have a resistence of 25 ohms or less?

Status
Not open for further replies.

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
HI have a question on UFER.
Is a UFER / CEE required to be proofed to show 25 ohms or less?
I am aware of the requirements of a plate or rod electrode.

Thanks
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Thanks Larry! .
It never ceases to amaze me what a EE will say. "


Either a 20 ft length of copper cable can be installed in the slab or a shorter length of copper cable can be bonded to the rebar which totals at least 20 feet in length. Again, it is all about achieving the maximum 25 ohms ground resistance. "
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Thanks Larry! .
It never ceases to amaze me what a EE will say. "


Either a 20 ft length of copper cable can be installed in the slab or a shorter length of copper cable can be bonded to the rebar which totals at least 20 feet in length. Again, it is all about achieving the maximum 25 ohms ground resistance. "
That is indeed monumentally stupid!
In addition to the second sentence, it does not recognize the requirement for a footer rather than just a slab and the exclusion if it does not have direct earth or other substrate contact. Not to mention rebar diameter and lack of coating.
 

drcampbell

Senior Member
Location
The Motor City, Michigan USA
Occupation
Registered Professional Engineer
I think the original concept might be that a Ufer ground doesn't require good conductivity with the Earth because the slab becomes an equipotential "earth"-reference point, much like the hull of a ship in fresh water.

Of course, coated rebar and corrosion of uncoated rebar do make me wonder about its performance.
 
Last edited:

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I think the original concept might be that a Ufer ground doesn't require good conductivity with the Earth because the slab becomes an equipotential earth-reference point, much like the hull of a ship in fresh water.

Of course, coated rebar and corrosion over its lifetime remain problematic.
(y)
The entire evolution of the Ufer ground, by Ufer, was to deal with high resistance desert soil.
The key is in the enormous surface area compared to other made grounds, just as with the ship's hull.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
(y)
The entire evolution of the Ufer ground, by Ufer, was to deal with high resitance desert soil.
The key is in the enormous surface area compared to other made grounds, just as with the ship's hull.
Agreed, I do not know how those words came from a EE. I do wonder where EE's come up with more stringent grounds like for Cell towers?
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Because the design of cell tower grounding allows them to withstand most direct lightning hits. The designs are based on physics.
 
Because the design of cell tower grounding allows them to withstand most direct lightning hits. The designs are based on physics.
I don't know Tom.....maybe partly, but I have seen (and had to install) GES at cell towers and needed to meet a spec of 5 ohms. I'm pretty sure that figure was pulled out of someone's posterior area...... besides my understanding is lightning doesn't "care" much about DC resistance.
 