We routinely use a 120v UPS in our control panels. The kind with receptacles on the load side. Is this classified as "Separately Derived", and do we have to somehow tie the load side neutral to the the enclosure ground?
Also, as a standard feature, our panel's control power is tied to the UPS via plug and cord. The plug end plugs into one of the UPS receptacles, and the other end is stripped back and landed on terminal blocks, for distribution of backed-up power within our control panel. The UPS power cord plugs into a receptacle, which is wired to a branch circuit outside our panel. If the UPS fails, the customer can unplug the UPS and remove it, and then the hardwired plug and cord can then be plugged into the now empty recepticle, and power is restored.
If we had wired the UPS as separetly derived, we would now have a neutral to case bond (a vilotation).
Also, as a standard feature, our panel's control power is tied to the UPS via plug and cord. The plug end plugs into one of the UPS receptacles, and the other end is stripped back and landed on terminal blocks, for distribution of backed-up power within our control panel. The UPS power cord plugs into a receptacle, which is wired to a branch circuit outside our panel. If the UPS fails, the customer can unplug the UPS and remove it, and then the hardwired plug and cord can then be plugged into the now empty recepticle, and power is restored.
If we had wired the UPS as separetly derived, we would now have a neutral to case bond (a vilotation).