I’m looking to use TC rated cable in ladder tray directly to a UPS for the feeders...does this fall under 336.10 #7 permitted use condition? Between a cable tray and the utilization equipment or device(s).
I’m looking to use TC rated cable in ladder tray directly to a UPS for the feeders...does this fall under 336.10 #7 permitted use condition? Between a cable tray and the utilization equipment or device(s).
I would say no because there is a separate definition for a Uninterruptible Power Supply (UPS) in article 100.
Anyway, the NEC allows up to a 6' transition of TC cable from tray to device as long as it is not subject to physical damage. Seems easy enough to ensure that.
I would say no because there is a separate definition for a Uninterruptible Power Supply (UPS) in article 100.
2017 NEC
Article 100 Definitions.
Uninterruptable Power Supply. A power supply used to provide alternating current power to a load to some period of time in the event of a power failure.
I would say no because there is a separate definition for a Uninterruptible Power Supply (UPS) in article 100.
A UPS does contain electronics and chemicals (batteries) but should be considered an assembly. There are many other codes that govern a UPS, the NEC has limited scope.
Anyway, the NEC allows up to a 6' transition of TC cable from tray to device as long as it is not subject to physical damage. Seems easy enough to ensure that.
Given the realities of power conditioning that accompanies the purpose of a UPS in a circuit, I don't see how one can exclude the "electronic purpose" that a UPS more generally serves. The actual "power failure" is really only a special single state of the other multitude of power states that require "conditioning".
Not sure what that analysis gains you. All components of an electrical system have an "electrical purpose".
2017 NEC
Article 100 Definitions.
Utilization Equipment. Equipment that utilizes electric energy for electronic, electrochemical, chemical, heating, lighting, or similar purpose.
336.12(2) points you to 336.10(7), so you should disregard the industrial establishment language.
Given the realities of power conditioning that accompanies the purpose of a UPS in a circuit, I don't see how one can exclude the "electronic purpose" that a UPS more generally serves. The actual "power failure" is really only a special single state of the other multitude of power states that require "conditioning".