Consider a small 120VAC fan, like this one:
http://www.jameco.com/webapp/wcs/st...toreId=10001&catalogId=10001&productId=102884
Say it is installed in an industrial control panel enclosure for cooling airflow.
It certainly looks and acts like a motor. But does it merit branch circuit protection per NEC 430.52 and NFPA79 7.2.10.1?
The above fan is rated 0.24A on 60Hz, so table 430.52 would suggest a 0.72A (rounded up to 1A) fast-acting fuse or a 0.42A (round up to 0.5A?) time-delay fuse.
I commonly see fans like these connected directly to the control power transformer, with no protection other than perhaps a 10A time-delay fuse in the ungrounded conductor of the transformer secondary.
Are there some exceptions under which this falls? Or is it just a case of "not important enough to enforce"?
Since the fan motor is marked "impedance protected" I do see that it is exempt from overload protection under 430.32(B)(4). I just don't see where it can be exempted from branch overcurrent protection.
If it does require branch overcurrent protection, does that rule out AGC (1/4" glass) fuses as well?
Thoughts and comments would be appreciated.
http://www.jameco.com/webapp/wcs/st...toreId=10001&catalogId=10001&productId=102884
Say it is installed in an industrial control panel enclosure for cooling airflow.
It certainly looks and acts like a motor. But does it merit branch circuit protection per NEC 430.52 and NFPA79 7.2.10.1?
The above fan is rated 0.24A on 60Hz, so table 430.52 would suggest a 0.72A (rounded up to 1A) fast-acting fuse or a 0.42A (round up to 0.5A?) time-delay fuse.
I commonly see fans like these connected directly to the control power transformer, with no protection other than perhaps a 10A time-delay fuse in the ungrounded conductor of the transformer secondary.
Are there some exceptions under which this falls? Or is it just a case of "not important enough to enforce"?
Since the fan motor is marked "impedance protected" I do see that it is exempt from overload protection under 430.32(B)(4). I just don't see where it can be exempted from branch overcurrent protection.
If it does require branch overcurrent protection, does that rule out AGC (1/4" glass) fuses as well?
Thoughts and comments would be appreciated.