Rslover

Member
I recently installed a 200 amp single phase entrance to supply an attached pool house and pool to an existiing structure. the inspector said I had to size my entrance conductors for a commercial space. I asked the reasoning for this and he replied: "Because they dont sleep here." Am I missing something here? In my mind, "attached" makes it part of the dwelling. Thanks in advance. Maybe the rule for old dogs applies to this "old" electrician.
 
Clarification please: The pool house is attached to the main house ? By what structural means is it attached ?
(breezeway, common wall, etc ?)
 
The inspector is right he just did not explain it well.

The NEC allows 120/240 volt service conductors and feeder conductors that supply all the power to a dwelling unit to be sized smaller than other applications.

Here is what the code section has looked like through the 2011 NEC. If you are on the 2014 things have changed.

310.15(B)(7) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services
and Feeders.


For individual dwelling units of one family,
two-family, and multifamily dwellings, conductors,
as listed in Table 310.15(B)(7), shall be permitted as
120/240-volt, 3-wire, single-phase service-entrance conductors,
service-lateral conductors, and feeder conductors
that serve as the main power feeder to each dwelling unit
and are installed in raceway or cable with or without an
equipment grounding conductor. For application of this section,
the main power feeder shall be the feeder between the
main disconnect and the panelboard that supplies, either by
branch circuits or by feeders, or both, all loads that are part
or associated with the dwelling unit. The feeder conductors
to a dwelling unit shall not be required to have an allowable
ampacity rating greater than their service-entrance conductors.
The grounded conductor shall be permitted to be
smaller than the ungrounded conductors, provided the requirements
of 215.2, 220.61, and 230.42 are met.

So the inspector is correct that a detached garage or detached pool house is not a dwelling unit so that code section cannot be used.
 
hence post #2 :D
Looks like is going to be a case of which violation depending on the clarification between detached or attached.
 
Attached in this case means incorporated into the house by block and mortar. Not detached in any form of the word. Part of the structure. Detached I would understand.
Sorry Guys, cant see this one the way any of you have explained it. Service was undersized initially or I would not have had to add this service. Should have been 400 amp to begin with. I would have increased the main entrance but AHJ had other ideas. Thanks for all the responses.
 
Attached in this case means incorporated into the house by block and mortar. Not detached in any form of the word. Part of the structure. Detached I would understand.
Sorry Guys, cant see this one the way any of you have explained it. Service was undersized initially or I would not have had to add this service. Should have been 400 amp to begin with. I would have increased the main entrance but AHJ had other ideas. Thanks for all the responses.
So the AHJ is allowing a second 120/240 service??? ...or is it just a second service entrance from the same service?

Either way, it still does not supply the entire dwelling load... so 310.15(B)(7) does not apply.
 
A building or structure is allowed only one service per 230.2. If the pool house is attached to the main structure (without appropriately rated fire walls) then a second service should not be allowed.
Without additional information, I am at a loss as to how a 2nd service was allowed but in the event it met the AHJ's criteria for a second service, then Bob's post in #3 comes into play and conductors have to be sized per 310.16 ('08 NEC) since they are not carrying ALL loads associated with the dwelling as required when using 310.15(B)(6)
 