greenville200
Member
- Location
- Attleboro MA
- Occupation
- Electrical Project Manager
We have a project with a 100HP fire pump 208V/120V 3PH. The fire pump controller is service entrance rated and has a separate disconnects for the utility feed and generator feed. The engineer has shown a 2000 amp switch board for the fire pump service, fed with 750MCM AL from the utility transformer. The switch board has arc energy reduction built in. The switchboard is in the electrical room. Then from the switchboard they show 2 sets of 250MCM AL feeding the utility power to the fire pump controller. My question is couldn't we just run the secondary from the utility transformer to a 400 amp Ct Cabinet in the electrical room and then from their go underground to the fire pump room into the fire pump controller? The fire pump controller specifications show no built in arc energy reduction. Or perhaps having the switchboard was put in by the engineer in order to provide a safer way to service the fire pump controller, but is not required by NFPA 20 or NEC 2020?
Any input on this would be appreciated.
Any input on this would be appreciated.