Tradesmanx
Member
- Location
- Sammamish, WA
My project has an 18 AWG multiwire shielded carol cable running from an automatic transfer switch to a generator. The cable has 10 wires in it and the jacket is rated at 300 volts. It has a CL3R UL listing label on it. We put it in the same conduit with the 6AWG wires that exchange power between the transfer switch and generator. NEC 300.3(A)1 says ac and dc can run in the same conduit as long as the insulation rating of the wires match or exceed the highest voltage applied to any conductor. But, the Head inspector is saying the cable can only be used exclusively for class 3 purposes. The 8500 watt generator is clearly a class one device. He wants us to pull the carol cable out and run it in a different conduit. In fact, I'm not even sure that will satisfy him. He may want me to run 10 thhn wires through conduit. Presumably, the CL3R listing would prohibit using the carol cable for the generator at all. I think he is wrong. I think the CL3R listing simply means it can also be used for class 3 and it isn't exclusive to other uses. What should I make of this?