Let's do this:
-Scenario 1.
3/4" emt conduit: 3 circuits #12awg 120V+G (6ccc)
More than 3ccc adjustment factor 80%
#12awg (30A----90°column)
30A*0.8=24A
I'm still good with 20A ocpd each circuit
-Scenario 2.
3/4" emt conduit: 3 circuits #10awg
120V +G (6ccc)
80% adjustment factor
#10awg (40A-----90°column)
40A*0.8=32A
I'm still good with 20A ocpd each circuit
In this cases:
1. For derating adjustment factor is correct to use 90° column ampacity?
2. The neutral conductor qualify as ccc?
Thanks all in advance
-Scenario 1.
3/4" emt conduit: 3 circuits #12awg 120V+G (6ccc)
More than 3ccc adjustment factor 80%
#12awg (30A----90°column)
30A*0.8=24A
I'm still good with 20A ocpd each circuit
-Scenario 2.
3/4" emt conduit: 3 circuits #10awg
120V +G (6ccc)
80% adjustment factor
#10awg (40A-----90°column)
40A*0.8=32A
I'm still good with 20A ocpd each circuit
In this cases:
1. For derating adjustment factor is correct to use 90° column ampacity?
2. The neutral conductor qualify as ccc?
Thanks all in advance