ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Consulting Electrical Engineer - Photovoltaic Systems
As long as I have been designing solar (12 years) I have been going by John Wiles' conductor sizing algorithm for 90 degree conductors, which is to say, I multiply the inverter output current by 1.25 and choose a 75 degree ampacity conductor size that exceeds it, then I choose a 90 degree conductor size whose conditions of use derated ampacity exceeds the inverter output current, and then I use the larger of the two wire sizes. Then I choose an OCPD which is the next size up from the conditions of use 90 degree ampacity of the chosen conductor.
I now have a commercial PV inspector who is invoking 110.14(C)(1)(b), claiming that it directs that the 75 degree ampacity of the conductors has to be equal to or greater than the rating of the OCPD. 110.14(C)(1)(b) is written with the same clarity and precision that we have come to expect from the NEC (ahem). Is he correct, and if so, can someone explain it to me in words of two or fewer syllables?
I now have a commercial PV inspector who is invoking 110.14(C)(1)(b), claiming that it directs that the 75 degree ampacity of the conductors has to be equal to or greater than the rating of the OCPD. 110.14(C)(1)(b) is written with the same clarity and precision that we have come to expect from the NEC (ahem). Is he correct, and if so, can someone explain it to me in words of two or fewer syllables?