Hello, I'm hoping someone can help me understand if the grounding for my house is adequate, room for improvement, or just plain wrong.
1) Meter box is grounded with ground wire and rod beneath it.
2) Three service cable 2/0 CU run to the main panel (two hots and a neutral.) (No ground wire) about 25 feet away.
3) The main panel 200amp is the first disconnect. The neutral and ground bars are bonded.
4) There is no other ground rod or ground wire to or from the main panel.
So I'm guessing that the neutral 2/0 cable between the panel and meter box would serve as the ground?
Is this good enough?
Would the grounding be improved if a separate ground and ground rod were added to main panel bonded ground/neutral bus bars in addition to the ground and ground rod at the meter box? Or can it only have a ground to ground rod in one and not both locations? Each of the grounding rods would be on different sides of the house.
I had the panel replaced and upgraded to 200 amp by licensed electrician about 5 years ago and this is how it was already configured. I did ask if it was properly grounded but was a little confused as its also a 1965 house, and we didn't rewire the entire house and bring everything up modern code.
The existing ground rod under the meter box is also 50 years old and under a concrete patio with the bare ground wire sticking up out of it, so not sure what condion its in. The electrictions said they would put a new one when they installed new 200 amp panel but didn't. Maybe they tested it? I have a multi meter but not sure if that would be sufficient to test the resistance.
Any insights or suggestions would be helpful with my planning and having work done. Does this seem like normal configuration and fine, or would adding reconfiguring be a good idea? Thanks!
1) Meter box is grounded with ground wire and rod beneath it.
2) Three service cable 2/0 CU run to the main panel (two hots and a neutral.) (No ground wire) about 25 feet away.
3) The main panel 200amp is the first disconnect. The neutral and ground bars are bonded.
4) There is no other ground rod or ground wire to or from the main panel.
So I'm guessing that the neutral 2/0 cable between the panel and meter box would serve as the ground?
Is this good enough?
Would the grounding be improved if a separate ground and ground rod were added to main panel bonded ground/neutral bus bars in addition to the ground and ground rod at the meter box? Or can it only have a ground to ground rod in one and not both locations? Each of the grounding rods would be on different sides of the house.
I had the panel replaced and upgraded to 200 amp by licensed electrician about 5 years ago and this is how it was already configured. I did ask if it was properly grounded but was a little confused as its also a 1965 house, and we didn't rewire the entire house and bring everything up modern code.
The existing ground rod under the meter box is also 50 years old and under a concrete patio with the bare ground wire sticking up out of it, so not sure what condion its in. The electrictions said they would put a new one when they installed new 200 amp panel but didn't. Maybe they tested it? I have a multi meter but not sure if that would be sufficient to test the resistance.
Any insights or suggestions would be helpful with my planning and having work done. Does this seem like normal configuration and fine, or would adding reconfiguring be a good idea? Thanks!