Is galvanized steel conduit required?

Status
Not open for further replies.

jgollner

New member
I'm an electrical contractor installing a generator in a Skilled Nursing Facility. The code section is 517-40 (1999 code used by the State of California). The size is 75 KW and the installation is outdoors (NEMA 3R). A question was raised by an Architect for a requiement to use only galvanized steel conduit for the emergnecy power. I an unable to locate it in NFPA 70 or NFPA 110. Has anybody seen this requirement?
 
Re: Is galvanized steel conduit required?

see 517.30 (C)(3) which lists the wiring metods, this is the 2005 NEC. PVC can be used if concrete encased
 
Re: Is galvanized steel conduit required?

see 517.30 (C)(3) which lists the wiring metods, this is the 2005 NEC
What is a skilled nursing facility?
Is this the same as a hospital?
If not, would 517.30(C)(3) even apply?
If so, wouldn't EMT or IMC be permissible since it's a "nonflexible metal raceway"?
 