scotteng
Member
- Location
- Apollo Beach, FL
- Occupation
- Professional Engineer
I have a client that uses a Power Soak unit, which is large tub of water with a motor and heater for recirculating hot water for pot and pan washing. https://www.youtube.com/watch?v=hmgyuydN940
The client connects the motor/heater via a HD-Pro GFCI unit. They also bond the branch circuit EG to the sink. This HD-Pro GFCI unit gives them trouble via false trips...probably due to motor leakage current.
The manufacturer states that the GFCI unit is not required. The client that it is due to NEC 680. I am of the belief that a wash tub doesn't fit within the scope of NEC 680 in that it is not a swimming pool, wading pool, therapeutic pool, decorative pool, fountain, hot tub, spa, hydro-massage bathtub or similar. Client feels immersion of employee hands in sink makes 680 applicable.
Any thoughts on applicability of NEC 680 or another section?
The client connects the motor/heater via a HD-Pro GFCI unit. They also bond the branch circuit EG to the sink. This HD-Pro GFCI unit gives them trouble via false trips...probably due to motor leakage current.
The manufacturer states that the GFCI unit is not required. The client that it is due to NEC 680. I am of the belief that a wash tub doesn't fit within the scope of NEC 680 in that it is not a swimming pool, wading pool, therapeutic pool, decorative pool, fountain, hot tub, spa, hydro-massage bathtub or similar. Client feels immersion of employee hands in sink makes 680 applicable.