Is GFCI required for not readily accessible dedicated outlets in greenhouse?

Status
Not open for further replies.
I am the electrician building aeroponic vertical farms inside shipping containers. We have high pressure water being sprayed inside enclosed growing panels, relative humidity around 65%, and a lot of electrical equipment. I am building these to feasibly sell anywhere in the country so I want to build to the highest interpretation of the NEC instead of my local AHJ viewpoint. I have found a lot of questions answered on this forum already that help me in navigating the NEC and other requirements, so thank you all.

I have receptacles installed in the overhead that are dedicated for 12 total circulating fans. I have this branch circuit from a 20 amp breaker supplying two strings of receptacles protected by GFCI receptacles. These GFCIs sporadically trip, if it happens for a long period of time such as overnight/weekend there is noticable crop damage resulting in lost merchandise. Understandably, my boss does not want this to happen, leading me on a long search of what I can do about it.

Reading the NEC and searching online forums including this one I think I can legally and safely remove the GFCI protection completely, but I want to make sure I am not leading myself to the wrong conclusion and above all i want to make sure it is still as safe as working with electricity can realistically be:
These are not dwelling units, and an argument could be made that they are agricultural buildings or standalone garages. These receptacles are not readily accessible based on the definition and needing a portable ladder to access, and the receptacles are for dedicated appliances (I would change out the duplex for single receptacles to meet this) I have read this exclusion mostly online and haven't been able to find a hard NEC reference yet, I would appreciate one if someone knows. 210.8(B) Exception 2 is close but that is specific to certain appliances. Can anyone provide validation or clear guidance in this?

From a practical standpoint and reading into the "not readily accessible and supply specific appliance" clause, it seems the hazard is plugging and unplugging the cord, not as much focused on the equipment developing a fault (the breaker would trip to protect the equipment/wiring)

Clearly I don't fall under Exception of removal of power introducing a greater hazard than the GFCI trip. Losing a few thousand dollars of crop is not on the same playing field as electrocution. I'm not trying to cut corners but find the correct level of protection and reliability.
 
How is the water being sprayed? On the plants directly or throughout the container?

How are these containers being powered?
 
I should of included this info. I would classify it as a damp location based on the definitions. These could be operated anywhere, so I have convinced myself to build to the highest reasonable conclusion a local AHJ would determine. I am pretty confident 98 out of 100 AHJ would agree with damp based on the informational note including barns and cold storage warehouses.
"Protected from weather" - they are indoor however I have pressurized water systems in the same shipping container.
"not subject to saturation with water or other liquids" - For normal usage no saturation, potentially an extremely light mist. If something malfunctioned they could be wetted or saturated. I suppose the same is true of dry locations and the definition is based on usage.
"Subject to moderate degrees of moisture" - the relative humidity is upwards of 60%, and there is potential for water mist to be in the air.

I am using extra heavy duty boxes and covers so it would be extremely unlikely for the receptacles to get wet even if there was a pipe burst ect...
 
How is the water being sprayed? On the plants directly or throughout the container?

How are these containers being powered?

Water is sprayed in contained enclusures directly on the plant roots, not on the exposed leaves or throughout the container.
IMG_20171115_104601313_HDR.jpg


They are powered with 240V single phase power coming in. As these are mobile containers, I have them powered off two independent 14-60 plug and receptacles (1 for air conditioner, 1 for the rest of farm in separate load centers - not conductors in parallel.)
As a side note to how they are being powered, I plan to soon outgrow the 60 amp limit of the readily available receptacles. I am confident I can NOT have a 70 amp OCPD to the 14-60, and would in fact have to upsize to a 100 amp plug connector such as IEC 309 4100P12W, if I am wrong that would be a great surprise.
 