We have a situation where a high school gymnasium's RTU is being replaced. We are in a northern climate, and it's quickly turning into winter, so a few weeks ago the team installed a temporary heater (ducted to an exterior gas-fired element) and temporary fan, which will remain in place until the RTU is replaced. I am told it should be complete by end of next week. The gym remains occupied for PE and after-school volleyball/basketball activities. The temporary equipment is currently installed via cord - I'm not familiar with it but sounds like it is connected via an NM or SO cord-and-plug to a 208V outlet installed for temporary power.
Today the inspector requested that the cord be removed and that the temporary equipment be fed via hard pipe (EMT). (For one week.) The construction team is asking us (design engineers) if this is a code requirement. Here's what I found:
NEC Article 590 governs Temporary Installations.
* 590.3 states we can't exceed 90 days, and we will not exceed that.
* 590.4(C) branch circuits allows multiconductor cords or cables. Type NM, NME and SE shall be permitted to be used in any dwelling, building or structure without any height limitation or limitation by building construction type and without concealment within walls, floor or ceilings.
* 590.4(H) requires protection from accidental damage. This seems to be mainly concerned with sharp corners and passing through doorways. I am not too concerned with volleyballs.
So I'm not a big expert on temporary power, but in reviewing 590 I think although the code allows for some areas of discretion/interpretation, our installation meets the letter and intent of the code. Maybe the cord needs swapped out with NM or SE if it is not already one of those. Obviously, at the end of the day the inspector is going to get what he wants, but this information at least gives the construction team some talking points to engage with the inspector. Any thoughts?
Thanks!
Today the inspector requested that the cord be removed and that the temporary equipment be fed via hard pipe (EMT). (For one week.) The construction team is asking us (design engineers) if this is a code requirement. Here's what I found:
NEC Article 590 governs Temporary Installations.
* 590.3 states we can't exceed 90 days, and we will not exceed that.
* 590.4(C) branch circuits allows multiconductor cords or cables. Type NM, NME and SE shall be permitted to be used in any dwelling, building or structure without any height limitation or limitation by building construction type and without concealment within walls, floor or ceilings.
* 590.4(H) requires protection from accidental damage. This seems to be mainly concerned with sharp corners and passing through doorways. I am not too concerned with volleyballs.
So I'm not a big expert on temporary power, but in reviewing 590 I think although the code allows for some areas of discretion/interpretation, our installation meets the letter and intent of the code. Maybe the cord needs swapped out with NM or SE if it is not already one of those. Obviously, at the end of the day the inspector is going to get what he wants, but this information at least gives the construction team some talking points to engage with the inspector. Any thoughts?
Thanks!