sparkyguy545
Member
Industrial Campus with Owner's MV distribution.
I will have a line-up of 5kv MV Metal-Clad vacuum swgr fed from two sources (Main-Tie-Main). Vacuum Breakers will be fully-interlocked to prevent paralleling sources. All downstream loads are 3-phase. There are no single-phase L-N loads involved, nor will there ever be.
Source #1 is low-resistance grounded at an exterior pad-mount transformer (center of Y connected to ground thru a grounding resistor).
Source #2 is 4160Y/2400, solidly grounded, fed from another exterior transformer.
Source #1 will consist of phase conductors and insulated ground in PVC ductbank. Since Source 31 is resistance-grounded there will be no grounded system conductor (neutral).
My question is in regards to Source #2:
Is it MANDATORY to install a grounded system conductor (neutral) between Source #2 and my Metal-Clad gear?
For installations below 1kv, I understand the general requirements in 250.24(C) which REQUIRES me to install a grounded system conductor (neutral) between source and the downstream gear. However, is there anything which REQUIRES me do do so for MV applications? If there is such a requirement, please clarify where noted in NEC.
Thanks in advance.
I will have a line-up of 5kv MV Metal-Clad vacuum swgr fed from two sources (Main-Tie-Main). Vacuum Breakers will be fully-interlocked to prevent paralleling sources. All downstream loads are 3-phase. There are no single-phase L-N loads involved, nor will there ever be.
Source #1 is low-resistance grounded at an exterior pad-mount transformer (center of Y connected to ground thru a grounding resistor).
Source #2 is 4160Y/2400, solidly grounded, fed from another exterior transformer.
Source #1 will consist of phase conductors and insulated ground in PVC ductbank. Since Source 31 is resistance-grounded there will be no grounded system conductor (neutral).
My question is in regards to Source #2:
Is it MANDATORY to install a grounded system conductor (neutral) between Source #2 and my Metal-Clad gear?
For installations below 1kv, I understand the general requirements in 250.24(C) which REQUIRES me to install a grounded system conductor (neutral) between source and the downstream gear. However, is there anything which REQUIRES me do do so for MV applications? If there is such a requirement, please clarify where noted in NEC.
Thanks in advance.