Is interrupting the neutral along with the lines ever required?

Status
Not open for further replies.

JMF

Member
Location
Tucson
Occupation
Engineer
Hi all. In a 4 wire 3 phase system, does the code ever require that the neutral be interrupted with the line conducors with a disconnect, either a 4-pole breaker or 4-pole disconnect?

I know that it is allowable to open the neutral, if all 4 poles open simultaneously, but is it ever required?

Thanks!
John
 

kwired

Electron manager
Location
NE Nebraska
Welcome to the forum...Been a long time but I believe it is required to switch the neutral on gas pumps.
Pretty much in all Class 1 hazardous locations AFAIK.

Any neutral to ground voltage present can spark if you touch them together and potentially ignite the mixture that caused the classification, if you happen to be servicing said equipment (which is a reason for having disconnecting means) to a point where you have exposed such possibility.
 