Is the only difference that 500 kcmils allows you to go up to a 380 amp load and 600 kcmils gives you that extra 20 amps from 380 – 400 amps if you happen to be in that range?
I agree with this statement.But for a feeder on a 400 amp OCPD, if the load falls in between 381 and 400 amps, then are 600 kcmils required? And if the load is under 381 amps then 500 kcmils are good.
I'll take Things That Some Electricians Say But Make No Sense for $200 Alex.I haven't used a lot of 600mcm.
Most times at those amperages we are paralleling, but, I was told that the stranding on 600 mcm actually makes it easier to work with than 500mcm.
Is that true?
JAP>
I haven't used a lot of 600mcm.
Most times at those amperages we are paralleling, but, I was told that the stranding on 600 mcm actually makes it easier to work with than 500mcm.
Is that true?
JAP>
Yes that's about it. Depending on length less voltage drop with the 600's. If you're feeding a 400 amp panel/OCPD from a transformer then you must use the 600's as the next size up rule is not permitted for 500's.
Hell No!
It is almost like 100mcm bigger! and bends like it too. Put your big boy pants on and have fun keeping stress off the breaker.
Do you have experience bending large wire?
Hell No!
It is almost like 100mcm bigger! and bends like it too. Put your big boy pants on and have fun keeping stress off the breaker.
Do you have experience bending large wire?
Yes, plenty. We routinely use up to 750 kcmil copper. I generally avoid the 750's like the plague, we have some younger guys to wrestle with that stuff. I do frequently work with 600's. Recently I had to deal with this disaster, 600 kcmil copper in an installation that they call "field conditions". Oh forgot to mention that the wire was pulled before the wireway was installed. :slaphead:
.
View attachment 23272
I see some of those bondless bonding bushings being used.
JAP>
Yup ran out the plastic ones.
If they increase the number of strands, maybe. Still large enough that it bends hard.I haven't used a lot of 600mcm.
Most times at those amperages we are paralleling, but, I was told that the stranding on 600 mcm actually makes it easier to work with than 500mcm.
Is that true?
JAP>
Nope, just regular copper SIMpull THHN/THWN-2 600 kcmil. Those are 4" EMT so the proportions are correct.
View attachment 23277