I apologize for not giving you enough info. Im learning here. Still pretty new to maintenance. The panelboard is rated to 1600A. The 800A breaker is just for this suite. Thats why I think it's 800A feed. I just didnt get why the panel in the suite "MDP" is only 350A. Shouldnt it be 800A panel since it's an 800A feed to the suite? Or is the panel only rated for the max load the suite is putting on the circuit. So if that only 350A panel, does that mean there is still 450A available for use on that circuit?
View attachment 12100
View attachment 12101
Here is the panel mounted on the roof. The 3rd one down is it. When I throw it it shuts down "MDP,A, and RTU 2" located in the suite. The breaker has 800A labeled on it. MDP is labeled and show on the print 350A. Why is there a 350A panel feed from a 800A. If this 800A breaker on the roof feeds 2 suits then would only 400A be available to each suite? That would explain the 350A "MDP" panel. This is a great discussion. Thank you.
That's not how it works. There are formulas and tables EEs use to determine how it is sized. Look at the breakers in your house. Yes, they add up to higher value than the service.
Go up another rung in the ladder.
Say each house is 200A and there are 10 houses to the transformer. If you just add things up, the transformer would have to be 480kVA, but there is no way you'll see a 500kVA transformer for a block with 10 house.
Yes, a coordinated block wide effort at the block level to get each house to turn on 40kW of all once will trip something or damage PoCo equipment.
There are formulas that address things at the individual building, block, subdivision level and in larger level. The formulas don't stay good forever, because of cultural change.
When the existing power system was designed, the coincidence factor did not consider modern, high demand customer loads such as electric car charging, tankless electric water heaters or practically every house having an A/C.