Here goes,
480V 3 phase MCC feeding a 7A breaker serving as a service disconnect in a MCC bucket, this feeds a motor starter with an overload module attached set for 1.7A (this is the FLA of the motor it protects) also in the MCC bucket. From the Overload module I have a conduit run of around 100' containing the T-Leads feeding the 1hp motor, this setup is existing and running.
The modification is to add a 120vac vibrator to a hopper near the motor which there is not an existing power source, so he wants to install an enclosure near the motor to house the stepdown transformer, this transformer (480v-120v) will be fed off of the existing wiring at the motor (100' from the motor starter and inserted into the existing circuit after the overload module not ahead of the motor starter). I am asking is this circuit design violating NEC by placing the transformer(unfused primary) in the circuit between the overload module and the motor. If so, why? If not, why not?
Thanks