Is it allowed for thr neutral wire to enter GFCI terminal from this side?

Status
Not open for further replies.
I understand that a GFIC receptacle cannot be reverse feed
through the load side because of the complex circuitry, but
Is it allowed for the neutral wire to enter GFCI terminal
from this side? see attachment
 

Attachments

  • shared nuetral.png
    shared nuetral.png
    131.7 KB · Views: 3
Note that since GFCI receptacles interrupt both grounded and ungrounded conductors, the neutral connection must be on the line side.

Sent from my XT1585 using Tapatalk
 
Why is it incorrect?

Sent from my SM-T350 using Tapatalk

It is incorrect because it clearly shows the neutrals wired to the line (or HOT side) of the receptacles. Look at the slots - smaller slot is ALWAYS the hot side.
 
The terminal where the neutral white wire is entering the receptacle is normally where the hot blk wire enters. very confusing for a trainee. lol

Well trainee, get this. In probably over 50 years in this trade I never looked at the slots to determine where the hot and neutral go. THE ONLY THING YOU SHOULD BE LOOKING AT ARE THE SCREW COLORS!!! NOT SILLY PICTURES! Silver is neutral and brass is hot!!

I'd like to see what you do with 3 and 4 way switches...

-Hal
 