Panel has 8" sq bonding plate from neutral buss to can; am I wrong putting neutral conductor on ground bar from seu feeder?
The only time the neutral can be connected to a buss that is connected to the can is on a service panel.
Does that answer your question ?
That's what this is, which is why it has the plate instead of a screw. I tried to explain that but didn't have the book with me. Thanks for the response.
Guy was adamant about failing something and after the 15th thing he was wrong on I finally gave in so we can get this customers power back on.
Apparently I misunderstood your question.
I thought you were questioning placing a neutral on a bar that was bonded to the can (as in some "service only" loadcenters).
I agree that a neutral should not be terminated on a grounding buss (terminal strip) that is designed for grounding terminals.
we agree...I misunderstood the OP.