Is it load side or supply side
Frank6172
Maryland
Engineer
Hi All,
We are trying to figure out if it's load side connection so supply side connection for this project. Here is the site situation:
1. It's an apartment complex with 3 separate buildings but there's only one utility meter located in building 1. The pad-mounted stepdown transformer is located next to building 1.
2. Building 1 has the 277/480V service with switchgear and utility service disconnect and there are (2) 277/480V to 120/208V transformers in the electrical room.
3. Building 2 and 3 are fed by those 2 transformers located in building 1 through trench and both buildings have main disconnects and MDPs.
We plan to use 208V inverters for building 2 and 3 and 480V inverters for building 1. We also want to do the interconnection at the main disconnect for each building.
Question: Are we doing the supply side connection or load side?
Sounds like you have a single 480Y/277V service.
If you connect your 480V inverters on the utility side of the existing service disconnect for that service, that would be a supply side interconnection. If you connect your 480V inverters on the load side of that existing disconnect, that would be a load side interconnection. All 208V inverters will be load side interconnected, as they are on the load side of that 480V service disconnect.
Cheers, Wayne
Cheers, Wayne
If the point of interconnection to the service is on the line side of the service disconnect, then the interconnection is a 705.11 (line side) one, but the inverter connection(s) to the PV AC disconnect is/are 705.12 (load side) connection(s).