Let me give you some context. I work for a satellite ground station manufacturer. We install very large full motion antenna systems. Our systems are supplied with a 100A breaker box, however depending on the configured options we may only require 25-30amps per leg (3-phase 208).
Our customers typically build the site to support the power requirements of their particular configuration. So if only 30 amps are required for the system as configured, the site contractor will install a dedicated 30A 3-phase breaker just for our antenna and a 10AWG feeder line or our 100A breaker box. Is this OK and compliant with NEC?
Our customers typically build the site to support the power requirements of their particular configuration. So if only 30 amps are required for the system as configured, the site contractor will install a dedicated 30A 3-phase breaker just for our antenna and a 10AWG feeder line or our 100A breaker box. Is this OK and compliant with NEC?